By Wolfgang Hilmer, Siemens Industry
In brief:
High voltage and current distortion are the topics of primary focus in the IEEE 519 standard, the most commonly used standard for limiting the harmonics in the electric industry. For purposes of this discussion, we’ll define harmonics as currents or voltages with frequencies that are integer multiples of the fundamental power frequency. For example, the 2nd harmonic on a standard 60 Hz frequency would be 120 Hz, and the 3rd would be 180 Hz. Any equipment using semiconductor switching devices, (UPS systems, computers and variable speed drives) produce harmonic currents. These harmonic currents produce no real work, but they take up capacity by inducing heat throughout the electrical distribution system. Harmonics increase operating cost through the extra heating in transformers, motors and wiring, and by increasing the air conditioning requirements to remove heat. The higher the harmonic distortion, the more problems, simply put. Harmonic mitigation is a key factor in controlling facility electrical operating costs today and will be, for the foreseeable future.
ADVERTISEMENT
IEEE 519 limits the demand distortion (THDD) and voltage distortion (THVD) at the point of common coupling (PCC). The VFD input current distortion (THID) doesn’t necessarily need to be less than 5% to meet IEEE 519 at the PCC (Figure 1).
Figure 1. IEEE 519-1992 Maximum Harmonic Current Distortion in % of Load |
Figure 2a and 2b. 400 hp, 6-pulse drive |
Especially in large power distribution systems and installations, in which the variable frequency drive isn’t the main load, six-pulse drives can meet IEEE 519 at the PCC, though sometimes harmonic mitigation is necessary. A range of solutions is currently available for this purpose, including passive and active harmonic filters, typically connected upstream of the VFD, plus drive topologies including multi-pulse rectifiers and active front ends.
On a typical drive, the motor-side inverter controls the motor, the DC link capacitor serves as the voltage source, and the front end charges the DC link. On the standard six-pulse drive, the input line reactor reduces line-side harmonics only by a limited amount, while the higher impedance results in lower harmonics. The THID at the input terminals typically is in the 40% range (Figure 2a and 2b). Let’s now look at three types of newer, low harmonic, variable frequency drives:
Figure 3. 400 hp, 18-pulse drive with bypass |
The 18-pulse VFD is a robust design with a good track record and typically is found in municipal water and waste processing facilities. The typical 18-pulse VFD has a phase-shifting autotransformer with nine-phase output and a high-impedance line reactor. It also includes an 18-pulse rectifier (3 x 6-pulse) as shown in Figure 3. The THID for such a drive typically is 5%, but some manufacturers supply a configuration that achieves a THID of 8%.
For true 18-pulse performance, the transformer secondary voltages and impedances must be identical, while the secondary phase shift must be perfect. If the line supply is connected directly to a single six-pulse bridge, but uses a phase-shifting transformer for the other two, the impedance imbalance results in a greater THID.
The VFD with active front end is fully regenerative, meaning it can feed braking power back into the supply system. It has low harmonic distortion, usually less than 3% THID, operates easily on a weaker power supply having voltage and frequency dips and sags, plus its control of reactive power can even assist in stabilizing a weaker power supply.