Natural gas piping pressure testing, purging and equipment restarts
Ten hazards and how to avoid them.
By Bryan Baesel and John Puskar, P.E.
1 of 2 < 1 | 2 View on one page
Whenever gas piping is repaired, extended or newly installed, it must be purged. The rules and best practices for handling these situations are often misunderstood, even by those conducting the work. This has caused much pain and suffering, including deaths, explosions and the loss of billions of dollars in industrial assets. This article seeks to clear up some misconceptions and provide the insights needed to make sure this work is done safely at your facility.
There are two codes that directly apply to this kind of situation. The first is OSHA 1910.147 for lockout/tagout of hazardous energy sources. Most people make some attempt to comply with this code, at least on the electrical side. In our opinion, it’s followed religiously for electrical equipment. It’s followed less than half the time for gas piping, steam and other things that could be dangerous in a pipe. Even when people try to isolate equipment correctly, they often do not understand the issues surrounding lubricated plug valves and their need to be sealed in order to hold properly. Lubricated plug valves (which represents 60 to 80% of natural gas piping system valves) have a small gap between the plug and the valve body. If the sealant is not applied annually, as required by code and the manufacturer, gas will leak past the plug even when the valve is in the closed position. Most plants do not have the knowledge or the equipment to seal these and have never sealed them in the life of the valve. Closing or locking out a valve in this condition does not necessarily isolate the energy source.
The other code that applies to this issue is NFPA 54 (found at and available for purchase from the National Fire Protection Association’s Web site, www.nfpa.org). This is also called the National Fuel Gas Code. It is a rather large document and takes some time to study and truly understand. Many consulting engineering firms and contractors do not understand the code and, in some cases, have not even heard of it. There seems to be little forethought given to the actual installation of the gas pipe and how the gas pipe will be put into service. Here are some highlights from NFPA 54 about getting piping into service or the more complex matter of adding to an existing system.
10 gas piping and equipment start‐up hazards and how to avoid them
Shown below are ten hazards involved in purging natural gas piping and how to avoid them. These tips and techniques should be incorporated into a comprehensive documented procedure for natural gas piping purging, piping system design and equipment start‐ups.
1. Purge points
Purge points are pipe nipples installed at strategic locations in the piping system for the purpose of introducing or removing nitrogen and natural gas at various stages of the process.
These are generally one-inch schedule 80 nipples with natural gas-rated ball valves on the ends. It is important to select locations or orientations to make sure these are not susceptible to damage from things like vehicle traffic (being run into with a tow motor or scissors lift).
2. Isolation points
You have to be very careful that fuel trains are not exposed to excessive pressures that can damage components during pressure testing. This can be done with the use of line blinds. Valves can be left open or leak through in the closed position. Blinds provide positive isolation and eliminate the possibility of damaging devices in a fuel train that are not rated for the elevated test pressures (like regulators and pressure switches).
3. Piping support
During repairs, sections of piping may be disconnected to allow the addition of tees or to install blinds. It is important to ensure that adequate pipe supports exist to ensure that sections of pipe will not fall when disconnected. The closest support may be on the other side of the disconnected joint.
4. Gaskets
NFPA 54 does not allow the reuse of flange gaskets even if they appear to be in good shape. To ensure leak-free joints, it is important that new gaskets are used, as well as properly rated bolts for the flanges. Remember, if you are mating up flanges, it is raised face to raised face and flat face to flat face.
5. Material Specifications
The air we breathe is 78% Nitrogen, but two full breaths of pure Nitrogen can kill you.
It is important that only proper rated pipe and fittings are used. Validate that reputable suppliers are used and material is free from manufacturing and installation defects. This includes pinholes in cast fittings, fittings with misaligned threads and pipe that is not of the proper grade.